Two mechanisms, and no way to tell which without checking.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Corrections checked in this pass

  • Verified the short free-head pile equilibrium against FHWA equations. The model now shows mechanism load and required moment resistance.

Checks needed for project use

  • A geotechnical reviewer must confirm drainage and stress basis, bearing-factor formulation, correlations and settlement influence factors. Partial factors and project-specific ground conditions are outside these teaching checks.
  • Establish section moment resistance, whether the short-pile mechanism is admissible, head restraint, soil layering, cyclic loading and serviceability before deriving a design resistance.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

Lateral pile response depends on the pile stiffness, ground response, embedded length and head restraint. A short, relatively rigid pile can rotate through the soil; a flexible pile develops bending along its length. Ultimate failure also depends on the section resistance and applied actions.

By the end of this lesson you should be able to

  • Compute the stiffness factor and the length ratio
  • Classify the pile and identify its mechanism
  • Say what happens in the range where neither solution applies

A laterally loaded pile can be idealised as a beam on a distributed spring foundation. Here kh = p/y is line-spring stiffness in kN/m², with p in kN/m. Convert a volumetric modulus ks in kN/m³ using the loaded width, kh = ksD.

T = (EI/kh)^¼ is a characteristic length. This teaching model uses L/T below about 2 for relatively rigid response and above about 4 for relatively flexible response. The boundaries depend on the chosen spring model and restraint assumptions. They do not prove a soil failure or pile hinge mechanism; that requires load and section-resistance checks.

Worked example

Classifying one pile at three lengths

Given

  • Concrete pile, D = 0.6 m, E = 30 GPa
  • Distributed line-spring stiffness kh = 5000 kN/m², defined by p = kh y with p in kN/m

Find

Whether the pile is rigid or flexible at 4 m, 5 m and 10 m

    Check yourself

    A pile has L/T = 5. Where does it fail?