The Chartership Forum

Foundation Engineering / The bearing capacity equation

Three terms, three sources of strength

Where the resistance actually comes from.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Checks needed for project use

  • A geotechnical reviewer must confirm drainage and stress basis, bearing-factor formulation, correlations and settlement influence factors. Partial factors and project-specific ground conditions are outside these teaching checks.
  • Shape/depth/inclination methods and loading direction need exact provenance and compatible assumptions. Current Eurocode 7/UK NA conformity and numerical model limits are not certified.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

The bearing capacity equation is usually met as a formula to be memorised. It is much better met as a statement about where resistance comes from — because then you can tell, before calculating anything, which term is going to matter and which is a rounding error.

By the end of this lesson you should be able to

  • State the three terms and what each represents
  • Identify which dominates in clay and which in sand
  • Explain why the width term disappears in undrained clay
The bearing capacity equation
qult=c Nc+q Nq+12 γ′ B Nγq_{ult} = c\,N_c + q\,N_q + \tfrac{1}{2}\,\gamma'\,B\,N_\gamma

What it calculates: Gross ultimate bearing pressure of a shallow foundation

c
Cohesion — c′ drained, or su undrained (kPa)
q
Effective surcharge for drained analysis; total surcharge for a total-stress undrained analysis (kPa)
γ′\gamma'
Effective unit weight of soil below founding level (kN/m³)
B
Foundation width — the shorter plan dimension (m)
Nc,Nq,NγN_c, N_q, N_\gamma
Bearing capacity factors, functions of φ′ alone (—)

This assumes

  • General shear failure — the mechanism of Module 3 actually forms
  • A strip footing, vertically and centrally loaded, on level ground
  • Homogeneous soil to a depth of at least the failure mechanism

In plain terms: Three independent sources of resistance, added. The addition is itself an approximation — the three mechanisms are not truly independent — but a conservative and long-established one.

Taking them in turn.

The cohesion term, c·Nc. Resistance from the soil's shear strength at zero normal stress. In undrained clay this is the whole story.

The surcharge term, q·Nq. Resistance from the weight of soil beside the footing, which must be lifted for the passive zone to move. Note what this means: burying a footing deeper increases capacity, and it does so through the ground alongside rather than beneath.

The self-weight term, ½γ′B·Nγ. Resistance from the weight of the soil within the failure mechanism itself. It is the only term containing B, which is why width helps in sand — and it is the term nobody agrees on.

Worked example

A strip footing in sand, term by term

Given

  • Strip footing, B = 2.0 m, founded at D = 1.0 m
  • Dense sand, φ′ = 35°, c′ = 0
  • Unit weight 19 kN/m³ above and below founding level
  • Water table well below the failure zone
  • Nγ taken from the Vesic form

Find

The gross ultimate bearing pressure, and which term dominates

Assumptions

  • General shear failure — reasonable for dense sand
  • No shape or depth factors, so the answer is conservative

    Practice

    A strip footing 1.5 m wide is founded 1.2 m deep in a clay with su = 60 kPa and unit weight 20 kN/m³. Using qult = 5.14·su + q for the undrained case, what is the GROSS ultimate bearing pressure, in kPa?

    Check yourself

    For a wide raft founded near the surface on dense sand, which term of the bearing capacity equation dominates?