The Chartership Forum

Reinforced Concrete Design / Columns and structural walls

Slenderness and second-order effects

When a column starts to notice its own deflection — and why that depends on how hard it is being pushed.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Checks needed for project use

  • A concrete-design reviewer must check the stated first-generation clauses, National Annex choices, detailing rules and factor sets. Numerical agreement alone does not establish code compliance.
  • Determine Kr and Kphi, creep, end-moment factors and minimum first-order moments from the actual design basis. The illustrated M2 is not an approved design moment.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

Everything in the previous lesson treated the column's geometry as fixed. It is not. A column under load deflects sideways, the axial force acts on that deflection, and the moment grows — which increases the deflection, which increases the moment. Whether this matters is not a property of the column alone: the same column is short under a light load and slender under a heavy one.

By the end of this lesson you should be able to

  • Explain second-order effects as a feedback loop
  • Calculate the slenderness ratio and the limiting slenderness
  • Explain why the limit depends on the axial load
  • Apply the minimum eccentricity
  • Calculate a second-order moment by the nominal-curvature method

What you should already know

  • The interaction diagram (previous lesson)
  • Euler buckling and effective length (Structural Analysis Fundamentals, Module 18)

The feedback loop

Apply a moment to a column and it deflects sideways by some amount e. The axial force N is now acting at an eccentricity e from the section, so it applies an additional moment N·e. That extra moment causes extra deflection, which causes extra moment.

The loop either converges — the deflection settles at a value larger than the first-order one — or it does not, and the column buckles.

For a slender column the amplification can be large. For a stocky one it is negligible. The whole of slenderness design is deciding which case you are in, and then either ignoring the effect or calculating it.

This is the same mechanism as Euler buckling, but with an important difference: a real concrete column has an initial moment, is not straight, and cracks as it bends. It does not sit at zero moment waiting for a critical load. It amplifies from the beginning.

Slenderness ratio
λ=l0i,i=IA=h12  for a rectangle\lambda = \frac{l_0}{i}, \qquad i = \sqrt{\frac{I}{A}} = \frac{h}{\sqrt{12}} \ \text{ for a rectangle}

What it calculates: How slender the column is, as a pure number.

l0
Effective length — the actual length times the end-condition factor (mm)
i
Radius of gyration about the axis of bending (mm)
h
Section depth in the direction of bending (mm)

This assumes

  • The effective length correctly reflects the real end restraints
  • The section is uncracked for the purpose of computing i — a simplification

In plain terms: For a rectangle, i = h/√12 = 0.289h, so λ ≈ 3.46 l₀/h. A 400 mm column with a 4.2 m effective length has λ = 36. The number on its own means nothing until it is compared with the limit — and the limit is where the interesting part lies.

Limiting slenderness
λlim=20 A B Cn,n=NEdAcfcd\lambda_{lim} = \frac{20\,A\,B\,C}{\sqrt{n}}, \qquad n = \frac{N_{Ed}}{A_c f_{cd}}

What it calculates: The slenderness below which second-order effects may be ignored.

n
Relative normal force — how hard the column is being squeezed (—)
A
Creep factor; 0.7 where the effective creep ratio is not calculated (—)
B
Reinforcement factor; 1.1 where the ratio is unknown (—)
C
Moment-ratio factor; 0.7 where the end moments are unknown (—)

This assumes

  • The default A, B, C values are conservative substitutes for calculated ones
  • Nationally determined; requires verification against the National Annex

In plain terms: The √n is the important part. The geometric slenderness λ is a column property; whether second-order effects may be neglected also depends on the load-dependent limit λlim. Quadruple the axial load and the limiting slenderness halves. A column that was comfortably short at the top of a building can be slender at the bottom, at identical size.

Worked example

Is this column slender?

Given

  • Column 300 mm × 400 mm, C30/37 (fcd = 17.0 N/mm²)
  • Storey height 5.25 m, braced, with end conditions giving l₀ = 0.8 × 5.25 = 4.2 m
  • Design axial load NEd = 1200 kN
  • Bending about the 400 mm axis; d = 350 mm

Find

Whether second-order effects must be included, and the additional moment if so.

Assumptions

  • A = 0.7, B = 1.1, C = 0.7 — the default values, all nationally determined
  • Kr = Kφ = 1.0 for this arithmetic illustration; calculate both factors for design, since creep can require Kφ > 1

    Practice

    A 350 mm square column has an effective length of 3.5 m. What is its slenderness ratio λ?

    Practice

    A column has Ac = 160,000 mm², fcd = 17.0 N/mm² and carries NEd = 1400 kN. What is the relative normal force n?

    Practice

    For that column, what is the limiting slenderness λlim? Take A = 0.7, B = 1.1, C = 0.7.

    Summary

    • A column deflects, the axial load acts on that deflection, and the moment grows
    • λ = l₀/i, and for a rectangle λ ≈ 3.46 l₀/h
    • λlim = 20ABC/√n — slenderness depends on the LOAD as well as the geometry
    • Quadrupling the axial load halves the limiting slenderness
    • Slender columns are the normal case in buildings, not an exception
    • A minimum eccentricity of max(h/30, 20 mm) always applies
    • The second-order moment moves the design point sideways on the interaction diagram