Reinforced Concrete Design / Serviceability: cracking, deflection and durability
Crack width and deflection
The two checks that decide whether a floor is a success — and the empirical rule that usually replaces one of them.
Lesson review: expert verification remains open
This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.
Corrections checked in this pass
- Corrected the modular ratio in crack-strain calculations and the elastic strain/stress figure.
Checks needed for project use
- A concrete-design reviewer must check the stated first-generation clauses, National Annex choices, detailing rules and factor sets. Numerical agreement alone does not establish code compliance.
- Check restraint, tension-stiffening assumptions, effective tension area, actual exposure and service action combinations.
These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.
Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.
Read the lesson register and outstanding review notesWhy this matters
Nobody complains that their office floor has an inadequate moment of resistance. They complain that the doors stick, the partition has cracked, and there is a visible line across the soffit. Serviceability is what the client actually experiences, and it governs the design of most concrete floors. It deserves better than being treated as a box-ticking exercise at the end of a calculation.
By the end of this lesson you should be able to
- Explain crack width as spacing times strain difference
- Say why bar spacing matters more than bar area
- Apply the span-to-depth rule and state what it is really doing
- Explain the two modifications and when they apply
- Decide when the rule is not good enough and a calculation is needed
What you should already know
- The cracked elastic section (previous lesson)
- Combinations of actions, especially quasi-permanent (Module 2)
Crack width is a geometric idea
Strip away the empirical dressing and the crack-width formula says something obvious.
Between two cracks, the steel stretches more than the concrete does — the steel is carrying tension while the concrete beside it is largely relaxed. That difference in extension has to go somewhere, and where it goes is into opening the cracks at each end.
So the width of one crack is the difference in strain between steel and concrete, accumulated over the distance between cracks:
What it calculates: The characteristic crack width at the surface.
- Maximum crack spacing (mm)
- Mean strain in the reinforcement (—)
- Mean strain in the concrete between cracks (—)
This assumes
- Quasi-permanent loading — this is a long-term effect
- The section is cracked and elastic
- The crack spacing expression is EMPIRICAL, a regression on measured crack patterns
In plain terms: The equation itself is exact — it is a definition. Everything difficult is in the two ingredients, and they are of different kinds. The strain difference is mechanics with an empirical tension-stiffening correction; the crack spacing is a pure curve fit. Knowing which is which tells you which parts you can reason about and which you must simply apply.
Why spacing matters more than area
The crack spacing expression has the form
sr,max = 3.4c + 0.425 k₁ k₂ φ / ρp,eff
and the two terms say two different things.
The cover term, 3.4c. A crack cannot be controlled by a bar it is far from. Deep cover means the bar's influence has dissipated by the time the crack reaches the surface, so cracks form further apart and open wider. Increasing cover for durability makes cracking worse — a genuine conflict between two serviceability requirements, and one you cannot resolve by adding steel.
The bar term, φ/ρp,eff. For a given area of steel, using smaller bars more closely spaced reduces this term. Each bar controls the concrete near it, so more bars means more, finer, better-distributed cracks.
Two beams with similar steel areas — one with 2 H32, one with 5 H20 — have nearly the same strength and quite different crack widths. The one with more, smaller bars cracks better.
This is why crack control is fundamentally a detailing problem rather than a calculation problem, and why the code offers deemed-to-satisfy tables of maximum bar diameter and maximum bar spacing as an alternative to the calculation. In most ordinary buildings those tables are what is actually used.
Worked example
Crack width in a beam at service
Given
- 300 × 500 beam, d = 450 mm, C30/37
- 3 H25 tension bars, As = 1470 mm²
- Cover to the link 35 mm, link diameter 8 mm, so cover to the main bar c = 43 mm
- Quasi-permanent moment Mqp = 70 kNm
- Cracked section from the previous lesson: x = 136.7 mm, z = 404.4 mm, αe = 6.09
Find
The calculated crack width.
Assumptions
- kt = 0.4 for long-term loading
- k₁ = 0.8 for ribbed bars, k₂ = 0.5 for bending
- Short-term modular ratio used, which is conservative for the strain difference
Deflection, and the rule that usually replaces it
Calculating deflection properly is hard. It requires the cracked stiffness, which varies along the span; tension stiffening between cracks; creep, which depends on age at loading, humidity and member thickness; and shrinkage curvature, which deflects a singly reinforced beam even with no load on it at all.
So the codes offer a shortcut: satisfy a span-to-effective-depth ratio and the deflection is deemed acceptable without calculation.
Worked example
Span/depth check on a 7 m beam — and what to do when it fails
Given
- Simply supported beam, span 7.0 m, d = 450 mm, b = 300 mm
- C30/37 concrete
- Tension steel required by the bending design: 1250 mm²
- Tension steel provided: 1470 mm² (3 H25)
- No compression steel; no brittle finishes
Find
Whether the beam passes the span/depth check.
Assumptions
- K = 1.0 for a simply supported beam
- ρ is based on the tension steel REQUIRED by the bending design
- The expression is empirical, and the constants are nationally determined
Practice
A simply supported beam has d = 500 mm and a basic span/depth ratio of 16.5. What is the maximum span it may have, in metres, with no modification factors?
Practice
A cantilever with d = 400 mm has a basic span/depth ratio of 18. What is its maximum length, in metres? Take K = 0.4.
Practice
A beam has σs = 200 N/mm² at quasi-permanent load, cover to the main bar 40 mm, H20 bars, and ρp,eff = 0.04. What is the maximum crack spacing sr,max, in mm?
Check yourself
Two beams have identical steel areas. Beam A has 2 H32; beam B has 5 H20 (slightly less area). Which cracks better, and why?
Summary
- wk = sr,max × strain difference — the equation is a definition, the spacing is a curve fit
- Cover dominates crack spacing: more cover means wider cracks
- For a given steel area, smaller bars closer together crack better
- Crack control is a detailing problem more than a calculation problem
- The span/depth rule is a screening device, not a deflection calculation
- Calculate deflection where it matters: long spans, brittle finishes, cantilevers, transfer structures
- A design that only passes after chasing modification factors should be calculated properly