Reinforced Concrete Design / Water-retaining and containment structures
Cracking before the tank is filled
Why the critical load case happens in the first three days, and the ratio that decides whether cracking is controlled at all.
Lesson review: expert verification remains open
This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.
Checks needed for project use
- A concrete-design reviewer must check the stated first-generation clauses, National Annex choices, detailing rules and factor sets. Numerical agreement alone does not establish code compliance.
- Containment specialist must verify tightness class, hydraulic-gradient limits, restraint model, early-age tensile strain capacity, long-term shrinkage and combined load/thermal effects. Simplified critical ratio does not by itself predict the actual number of cracks.
These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.
Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.
Read the lesson register and outstanding review notesWhy this matters
Everything so far has designed for a load. A water-retaining structure has a load case that involves no load at all: the concrete heats as it hydrates, cools, tries to contract, and cannot — because it is cast against something older that will not move with it. The crack that results forms within days, before the tank has held anything, and it is usually worse than anything the water will do afterwards.
By the end of this lesson you should be able to
- Explain why serviceability governs completely here
- Derive the critical steel ratio from what happens at the first crack
- Say what changes either side of it
- Calculate a restrained thermal strain
What you should already know
- Crack width as spacing times strain (Module 6)
- Minimum reinforcement (Module 4)
- Shrinkage and thermal movement (Module 6)
A different failure
Ask what failure means for a water tank. It is not collapse — a tank wall designed for its hydrostatic pressure has an enormous margin against rupture. It is leakage, and a tank leaks through a crack far too fine to threaten its strength.
Crack width can govern the design, but hydrostatic resistance, stability and other ultimate checks remain necessary. That is the same inversion as prestressed concrete, arrived at for a completely different reason.
And the crack that matters is usually not caused by the water.
From first principles
The critical steel ratio
We want to show: To find how much reinforcement is needed before cracking becomes distributed and fine, rather than concentrated in one wide crack.
Picture a bar of concrete with a single reinforcing bar down the middle, gripped at both ends and cooled so it wants to shrink but cannot. Tension builds in the concrete. At some point it reaches the concrete's tensile strength and a crack forms. At that instant the concrete either side of the crack lets go of the tension it was carrying — and every bit of that force lands on the steel crossing the crack. Now there are two possibilities, and they lead to completely different structures. If the steel yields under that sudden force, it stretches without limit. The crack opens wide, the rest of the bar relaxes, and nothing else ever cracks. One crack, very wide. If the steel does not yield, it takes the force elastically, transfers it back into the concrete a little further along through bond, and that concrete cracks too. Then again. Many cracks, each fine. So there is a threshold, and it is simply whether the steel can carry what the concrete lets go of.
Where the strain comes from
Concrete generates heat as the cement hydrates. A 400 mm wall in plywood formwork might rise 30°C above ambient in the first day, then cool over the next few. As it cools it wants to contract — and if it is cast onto a mature base slab, it cannot.
ε = R · α · T₁ · K
- T₁ is the temperature rise and subsequent fall. It depends on the cement content, the section thickness and the formwork. It belongs to the concrete specification.
- α is the coefficient of thermal expansion, about 12 × 10⁻⁶ per °C.
- K is a creep relief factor, about 0.65. Young concrete relaxes a substantial part of the stress as it develops — which is genuinely helpful and is why the cracking is not worse than it is.
- R is the restraint factor, and it is the only one a structural designer really controls.
A wall cast onto a mature base is restrained at about R = 0.5 at the joint, falling towards zero at the top. Casting in shorter bays, or leaving a gap and filling it a fortnight later, reduces R directly — which is why bay sizes and pour sequences appear on structural drawings for water-retaining work and nowhere else.
Worked example
Early thermal cracking in a tank wall
Given
- Wall 400 mm thick, C30/37, cast onto a mature base slab
- 40 mm cover, H16 bars at 140 mm centres on each face
- Temperature rise and fall T₁ = 30°C; restraint factor R = 0.5
- Tensile strength at 3 days fct,eff = 1.8 N/mm²
- Water 6 m deep against the wall
Find
Whether the cracking is controlled, and whether the width is acceptable.
Assumptions
- Illustrative restraint factor R = 0.5 at the base joint
- α = 12 × 10⁻⁶ per °C; creep relief K = 0.65
- Crack-width limits are nationally determined and require verification
Predict first
A restrained wall has a steel ratio of 0.25%, below the critical 0.36%. A crack-width calculation gives 0.15 mm. What should you conclude?
Practice
A concrete has a tensile strength of 1.6 N/mm² at the age cracking is expected, with grade 500 steel. What is the critical steel ratio, as a percentage?
Practice
A wall is restrained at R = 0.5 with a temperature drop of 35°C. Taking α = 12 × 10⁻⁶ and K = 0.65, what is the restrained strain, in microstrain?
Practice
A 400 mm wall has 40 mm cover and H16 bars. What is the surface zone hc,eff used for crack spacing, in mm?
Summary
- Leakage can govern serviceability; ultimate resistance and stability remain essential checks
- The critical crack usually forms in the first days, before filling
- ρcrit = fct,eff/fyk, and it uses the EARLY-AGE tensile strength
- Below it: one wide crack, and the width formula is meaningless
- ε = R α T₁ K, and R is what a designer actually controls
- Minimum steel uses half the section; crack spacing uses the surface zone