The Chartership Forum

Structural Steel Design / Beam-columns and frame stability

Frame stability, and which moments get amplified

The same effect at the scale of a whole frame. It turns into a question about lateral stiffness — and about which moments the amplifier is allowed to touch.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Corrections checked in this pass

  • Minimum first-order moment retained; examples explicitly sinusoidal with Cm=1; signed sway combination and alpha-cr>=3 scope enforced; invalid boundary state withheld in UI.

Checks needed for project use

  • A steel-design reviewer must check the first-generation calculation profiles, second-order analysis assumptions, connection rules and execution references against the applicable standards and amendments.
  • Actual Eurocode interaction factors, cross-section class, member buckling, real moment distribution and restraint model. Sinusoidal magnification is not a general envelope.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

A member bows and its axial force acts through the bow. A frame leans and its whole vertical load acts through the lean. It is the same mechanism, and at frame scale it is measured by a single number that can be read off a first-order analysis: αcr. What makes it worth a lesson of its own is that the remedy is different. A member that fails on amplification usually needs restraint or a bigger section. A frame that fails on αcr needs stiffness, and no amount of member design supplies it.

By the end of this lesson you should be able to

  • Calculate αcr for a storey from its drift under horizontal load
  • Explain αcr as a comparison of two stiffnesses
  • Say when second-order analysis is required and why the threshold differs for plastic analysis
  • Apply the amplifier to the sway moments and not to the gravity moments
  • Convert an αcr shortfall into the stiffness change it actually demands

What you should already know

  • The magnification series and αcr (Module 4)
  • Equivalent horizontal forces from sway imperfections (Module 4)
  • The amplification factor from the previous lesson

αcr is a ratio of two stiffnesses

For a storey, the critical multiplier can be written straight from a first-order analysis:

αcr = (HEd / VEd) · (h / δH)

where HEd is the horizontal force on the storey, VEd the vertical force, h the storey height and δH the relative sway of the storey under HEd.

Grouped differently, it reads much better:

αcr = (HEd / δH) ÷ (VEd / h)

H/δ is the storey's lateral stiffness — force per unit sway. That is what resists the lean.

V/h is the rate at which the vertical load converts sway into overturning — a destabilising stiffness, with the same units. That is what causes it.

So αcr is simply the ratio of the stiffness you have to the destabilising effect you must resist. At αcr = 1 they are equal and the storey has nothing left. At αcr = 10 the lateral stiffness is ten times what the vertical load is consuming, and the amplification is 1/(1 − 0.1) = 1.11.

This reading is worth more than the formula, because it tells you what to change. αcr is proportional to lateral stiffness and inversely proportional to vertical load. If a storey is too flexible, you need stiffness — bracing, a stiffer frame, a core — and adding steel to columns barely moves it.

Try it

Drift, αcr, and where the moments go

A 4 m storey under 180 kN of horizontal force. Change the drift and the vertical load and watch αcr move. Then change how much of the moment is sway moment, and see what the two common shortcuts cost.

22 mm
4,200 kN
31 %

Global analysis

Design moment under the three amplification choicesamplify nothing305 kNmsway only319 kNmamplify everything350 kNmcritical multiplier 7.79 · amplifier 1.147 · swaygravity 210 + sway 95 kNm
Storey drift δ
22 mm
Critical multiplier αcr
7.79
Classification
SWAY
Sway amplifier
1.147
Second-order analysis required
YES
Design moment, sway only
319 kNm
If everything amplified
350 kNm
If nothing amplified
305 kNm
Cost of over-amplifying
9.7 %
Error from not amplifying
4.4 %
Stiffness needed for the threshold
1.28 ×

αcr = 7.79: first-order sway moments must be amplified by 1.15, or a second-order analysis used. The storey drift of 22.0 mm is what drives this — stiffness, not strength, is the governing quantity.

Things worth trying

  • Start at 22 mm. αcr = 7.79, the storey is a sway frame, and the three bars are 305, 319 and 350 kNm — the two shortcuts bracket the right answer on either side.
  • Take the drift down to 12 mm. αcr crosses 10 and the classification flips to non-sway. Nothing about the frame has changed except its stiffness — the threshold is a decision about acceptable error, not a physical boundary.
  • Now switch to plastic analysis at the same drift. Nothing changes — and that is worth knowing. The Eurocode RECOMMENDS a higher threshold for plastic analysis (15 against 10), on the reasoning that plastic redistribution softens the frame beyond what the elastic αcr predicts. The UK National Annex, NA.2.9, replaces it with 10 for clad structures, so in the UK the method does not change the classification.
  • Where the method DOES still change it is a portal frame under gravity loads only, which NA.2.9 relaxes all the way to 5 — subject to limits on span and rise. That relaxation carries conditions, so this lab does not apply it automatically.
  • Push the drift to 60 mm at 8000 kN. αcr falls towards 1 and the storey approaches instability. No member design fixes that — the storey needs stiffness.
  • Set the sway share to 100%. The 'sway only' and 'amplify everything' bars converge, because there is nothing else to amplify wrongly.
  • Now set it to 10%. Amplifying everything becomes expensive and amplifying nothing becomes almost harmless — which is exactly why the two errors are so often made in the wrong situations.
  • Watch the stiffness figure as you move the drift. It is the most useful number here, because it converts a failed check into the design change that would fix it.

Worked example

A storey that is too flexible

Given

  • A storey of a moment-resisting frame, 4.0 m high
  • Total horizontal force at the storey HEd = 180 kN, including the equivalent horizontal force from the sway imperfection
  • Total vertical force at the storey VEd = 4200 kN
  • First-order relative sway under HEd: δH = 22 mm
  • Column design moments: 210 kNm from the gravity (non-sway) case, 95 kNm from the sway case
  • Elastic global analysis

Find

Whether second-order effects must be included, and the design moment if so.

Assumptions

  • The αcr threshold is calibrated and nationally determined — held in the profile, unverified here
  • The amplified sway method assumes the sway deflection has essentially the shape of the sway buckling mode

    Member and frame effects are different problems

    Both are second-order effects and both use the same 1/(1 − ratio) form, which makes them easy to conflate. They behave completely differently in design.

    Member (P–δ)Frame (P–Δ)
    What deflectsThe member, between its endsThe whole storey, sideways
    Driving ratioNEd/Ncr for the member1/αcr for the storey
    Made worse byA slender memberA flexible frame
    Fixed byRestraint, or a stiffer memberBracing, or a stiffer frame
    Grade helps?NoNo
    Visible in a first-order analysis?NoNo, but αcr can be read from one

    The last row is the practical one. Neither effect appears in the output of a linear analysis, but the frame effect can be diagnosed from one in a single line of arithmetic, which is why αcr is worth computing early on every project. There is no equally cheap test for the member effect — it has to be checked member by member.

    And they must not be counted twice. If the analysis is genuinely second-order and includes the sway, the frame effect is already in the results and must not be amplified again. Module 4's allocation table is the discipline that keeps this straight.

    Practice

    A storey carries VEd = 4200 kN, is 4.0 m high, and sways 22 mm under a horizontal force of 180 kN. What is αcr?

    Practice

    What is the sway amplification factor at αcr = 7.79?

    Practice

    Gravity moments are 210 kNm and sway moments 95 kNm. With an amplifier of 1.147 applied correctly, what is the design moment in kNm?

    Practice

    A storey has αcr = 7.79 and drifts 22 mm. What drift would be needed to reach αcr = 10, in mm?

    Check yourself

    A storey has αcr = 6. The engineer increases every column size by one serial size and re-runs the analysis. What is the most likely outcome?

    Summary

    • αcr = (H/V)(h/δ) — the storey's lateral stiffness against the destabilising rate
    • It can be read from a first-order analysis in one line
    • αcr = 7.79 in the worked example: a sway frame, amplifier 1.147
    • Amplify the SWAY moments only: 210 + 1.147 × 95 = 319 kNm
    • Amplifying everything gave 350 kNm (9.7% wasteful); amplifying nothing gave 305 (4.4% unsafe)
    • Reaching αcr = 10 needed 1.28 times the lateral stiffness — a bracing decision
    • The threshold differs for plastic analysis because redistribution softens the frame
    • Member and frame second-order effects are the same algebra and different design problems