Structural Steel Design / Beams and lateral-torsional buckling
Restraint, moment shape, and where the load sits
Three things change the answer. One is free, one is decided by the structure, and one is a detailing choice most people never think about.
Lesson review: expert verification remains open
This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.
Checks needed for project use
- A steel-design reviewer must check the first-generation calculation profiles, second-order analysis assumptions, connection rules and execution references against the applicable standards and amendments.
- Check torsional/U-frame restraint, compression-flange restraint, brace stiffness and load height assumptions. End restraints and segment moment distributions require independent stability assessment.
These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.
Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.
Read the lesson register and outstanding review notesWhy this matters
The 8 m beam of the last lesson lost two thirds of its capacity. All three of the things that would recover it are available to a designer, and one of them — where the load is applied relative to the shear centre — is a decision usually made without any thought at all. It is worth 26% on this beam.
By the end of this lesson you should be able to
- Calculate what a lateral restraint buys, and when it stops buying
- Explain why uniform moment is the worst case
- Quantify the load-height effect and say which way it goes
- State what a restraint must physically do to count
Restraint: the largest lever, and it saturates
Mcr depends on the length between points of lateral restraint, not on the span. So a restraint at midspan halves the length that matters.
For the 8 m beam of the last lesson, restraining the compression flange gives:
| Restraints | Segment | λ̄LT | χLT | Mb,Rd | Gain |
|---|---|---|---|---|---|
| 0 | 8.00 m | 1.69 | 0.351 | 290 kNm | — |
| 1 | 4.00 m | 0.96 | 0.727 | 600 kNm | 2.07× |
| 2 | 2.67 m | 0.66 | 0.890 | 735 kNm | 2.54× |
| 3 | 2.00 m | 0.50 | 0.960 | 793 kNm | 2.74× |
| 5 | 1.33 m | 0.34 | 1.000 | 826 kNm | 2.85× |
| 7 | 1.00 m | 0.25 | 1.000 | 826 kNm | 2.85× |
One restraint at midspan more than doubles the resistance. That is a larger gain than any change of section or grade would give, and it costs a tie and two cleats.
And then it saturates. Once χLT reaches 1 the beam has its full cross-section resistance and there is nothing left to recover — the fifth restraint achieves the last 4%, and the seventh achieves nothing at all. Restraint is worth adding until χLT approaches 1, and pointless afterwards.
Worked example
Three ways to recover the same beam
Given
- The 8 m beam from the previous lesson: Mc,Rd = 826 kNm, unrestrained Mb,Rd = 290 kNm
- The load is a UDL, so the moment is not uniform
- It is a floor beam, so the load arrives on the top flange
Find
The effect of each of the three levers, separately.
Assumptions
- C₁ = 1.13 for a UDL and C₂ = 0.45 — both calibrated and unverified here
- The restrained case assumes the restraint is effective, per the callout above
Try it
Three levers on the same beam
The 8 m beam from the worked example, at 290 kNm against a cross-section resistance of 826. Restraint, moment shape and load height all move it — and only one of them is under full control.
Moment shape
Load applied at
- Segment length
- 8.00 m
- Moment factor C₁
- 1.00
- Load height zg
- 0 mm
- Critical moment Mcr
- 290 kNm
- LTB slenderness λ̄LT
- 1.688
- Reduction χLT
- 0.351
- Design resistance Mb,Rd
- 290 kNm
- Cross-section resistance
- 826 kNm
- Gain over the reference
- 1.00 ×
- Still lost to LTB
- 65 %
Mb,Rd = 290 kNm, which is 1.00 times the unrestrained reference case and 65% short of the cross-section resistance. There is still 536 kNm to recover.
Things worth trying
- Start from the reference case — no restraints, uniform moment, load at the shear centre. 290 kNm against a cross-section resistance of 826: two thirds gone.
- Add ONE restraint. The resistance more than doubles, to about 600 kNm. That is a bigger gain than any change of section or grade, for a tie and two cleats.
- Keep adding restraints. The gains shrink fast, and by five χLT reaches 1 and they stop entirely. Restraint is worth adding until χLT approaches 1 and is wasted afterwards.
- Go back to zero restraints and switch the moment shape to double curvature. C₁ = 2.6 and the resistance nearly doubles — because with equal and opposite end moments only a short length near each end is heavily compressed on the same flange.
- Now set the moment shape to UDL and move the load between the three positions. Top flange to bottom flange is a factor of about 1.7 — from a detailing arrangement that most people never calculate.
- Try all three levers together: one restraint, UDL, load at the bottom flange. The three multiply, and the beam becomes a completely different member from the reference case despite identical section, span and total load.
Practice
An 8 m unrestrained beam has Mb,Rd = 290 kNm. One restraint is added at midspan, taking χLT from 0.351 to 0.727. What is the new Mb,Rd, in kNm? Take Mc,Rd = 826 kNm.
Practice
For a UDL, C₁ = 1.13. If Mcr under uniform moment is 290 kNm, what is it under the UDL?
Practice
Top-flange loading gives Mb,Rd = 239 kNm and bottom-flange loading 408 kNm on the same beam. By what factor do they differ?
Check yourself
A beam has χLT = 0.96 with three restraints. What does adding a fourth achieve?
Summary
- Mcr depends on the length between RESTRAINTS, not the span
- One restraint at midspan more than doubled the resistance of the 8 m beam
- Gains saturate once χLT reaches 1 — beyond that, nothing is available
- Uniform moment is the worst case; C₁ = 1 is the reference and everything else is better
- Top-flange loading is destabilising and cost 26%; bottom-flange loading gains 37%
- Top versus bottom is a factor of 1.71 on this beam, from a detailing arrangement
- The three levers multiply — a restrained UDL beam is a different member entirely
- A restraint must reach the COMPRESSION flange, which changes side over a support