The Chartership Forum

Structural Steel Design / Cross-section resistance

Tension, compression, and the holes you drilled

A tension member is the simplest thing in structural steel, right up to the point where you connect it.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Checks needed for project use

  • A steel-design reviewer must check the first-generation calculation profiles, second-order analysis assumptions, connection rules and execution references against the applicable standards and amendments.
  • Confirm UK first-generation member net-section factor1.10 independently and thickness-dependent strengths; connection block tearing factor remains separate. Yielding/fracture labels do not guarantee visible warning or time to react.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

An ideal member in concentric tension does not buckle in that load case. A real member may also experience eccentricity, bending or load reversal, which need separate checks. Bolt holes reduce the net section and can make fracture govern instead of gross-section yielding. Compare the relevant member and connection resistance limits using the stated geometry, material properties and design factors.

By the end of this lesson you should be able to

  • Calculate gross yielding and net fracture, and say which governs
  • Explain why they carry different partial factors
  • Compute how much hole loss a grade will tolerate
  • Calculate block tearing and read what its two terms mean

What you should already know

  • Net area, including staggered holes (Module 1 library; Structural Analysis Fundamentals, sections)
  • Cross-section classification (Module 5)
  • The von Mises criterion, at least as τy = fy/√3 (Module 1)

Two limit states with different characters

A tension member can fail in two ways, and they are not variants of each other.

Gross yielding. The whole member reaches fy and stretches.

Npl,Rd = A fy / γM0

This is ductile. The member elongates visibly — remember from Module 1 that steel goes to about 15% strain — so it sags, the cladding cracks, and somebody notices. It also redistributes: a yielding member sheds load to stiffer paths.

Net-section fracture. The reduced section at the holes reaches fu and tears.

Nu,Rd = 0.9 Anet fu / γM2

This is brittle. It happens at one cross-section, at a strain the eye cannot see, and there is no warning and no redistribution.

The 0.9 is calibrated — it allows for the stress concentration around the holes and the eccentricity a bolt group introduces. It is not derivable.

Why the partial factors differ

γM0 = 1.0 for yielding and γM2 = 1.25 for fracture, and that gap is deliberate. A limit state you can see coming needs less margin than one you cannot. The code is arranged so that yielding governs wherever possible, and the extra 25% on the fracture side is part of how it arranges it.

Worked example

A bolted tie, and what the holes cost

Given

  • Flat tie, 200 × 25 mm, gross area 5000 mm²
  • S355: fy = 355 N/mm², fu = 510 N/mm²
  • Two 22 mm holes in one line across the member
  • γM0 =1.0, γM2,net=1.10 for member net-section fracture

Find

Which limit state governs, and by how much.

Assumptions

  • Holes in a single line, so no stagger credit
  • Partial factors in general UK use, not verified against the National Annex here

    Try it

    Yield or fracture?

    Two resistances, and the smaller one decides both the capacity and the character of the failure. Add a single hole and watch how quickly the brittle case takes over.

    200 mm
    25 mm
    2
    22 mm

    Steel grade

    Gross yielding against net-section fracturegross yielding1775 kNnet fracture1627 kNBRITTLE — it tears at the holesnet/gross = 78.0% · crossover at 96.7%
    Gross area A
    5000 mm²
    Net area Anet
    3900 mm²
    Area lost to holes
    22.0 %
    Crossover: max loss allowed
    3.3 %
    Yield ratio fu/fy
    1.44
    Gross yielding Npl,Rd
    1775 kN
    Net fracture Nu,Rd
    1627 kN
    Design resistance Nt,Rd
    1627 kN
    Governed by
    net fracture

    Net fracture governs at 1627 kN, below the 1775 kN gross yielding load. The member will fail at the holes, suddenly and without warning. Consider adding material at the connection so that yielding governs instead.

    Things worth trying

    • Set the holes to zero. Gross yielding governs, as it must — there is no net section to fracture. Now add ONE hole and watch how far the fracture bar drops.
    • Read the two percentages under the chart. The crossover for S355 is at 96.7% of the gross area, so you may remove only 3.3% before the brittle case takes over. A single line of two holes usually removes far more.
    • Change the grade and watch the crossover move. It is governed by the yield ratio fu/fy, not by the grade number — S275 at 1.56 tolerates the most, S355 at 1.44 the least. Specifying a stronger steel makes this WORSE.
    • Widen the plate while keeping the holes the same. The proportion lost falls, and eventually yielding governs again. This is exactly why tension members are widened locally at their connections.
    • Increase the hole diameter from 22 to 26 mm. A small change in the bolt size moves a substantial amount of area, because the loss scales with the diameter directly.
    • Note that the DESIGN RESISTANCE is always the lower bar — but the character of the failure changes with which bar that is. Two members of the same capacity can behave completely differently.

    Block tearing: a lump comes out

    A third failure is possible at a bolted connection, and it is neither of the above. Instead of the member failing across its width, a block of plate containing the bolts tears out of it.

    The block is bounded by two kinds of face, and they fail differently:

    • the tension face, across the end, which fractures at fu;
    • the shear faces, running along the bolt lines, which yield at fy/√3.

    Veff,Rd = fu Ant/γM2 + (fy/√3) Anv/γM0

    That expression is worth pausing on because it is unusual: it adds an ultimate term to a yield term, with different partial factors. Most interaction expressions do nothing of the sort. It is not a fudge — it is a statement that the two faces really do reach different limit states at the same instant, and the √3 comes straight from von Mises.

    Block tearing tends to govern when the bolts are close to the end of the member, because the shear faces are then short. It is also easy to miss, because neither the member check nor the bolt check will find it — it is a failure of the plate around the bolts, and it needs its own calculation.

    Practice

    A 5000 mm² tie in S355 has 3900 mm² net area. What is the net-fracture resistance, in kN? Take fu =510N/mm² and the stated UK member net-fracture factor γM2,net=1.10.

    Practice

    For S275 (fy = 275, fu = 430), what minimum fraction of the gross area must remain before net fracture governs? Take γM0 = 1.0 and γM2,net = 1.10 — EN 1993-1-1 §6.1 as set by the UK National Annex, not the 1.25 that applies to bolts.

    Practice

    A block of plate has 900 mm² net tension area and 2400 mm² net shear area, in S355. What is the block tearing resistance, in kN? Take fu = 510, fy = 355, γM0 = 1.0, γM2 = 1.25.

    Check yourself

    Why does net-section fracture carry a larger partial factor than gross yielding?

    Summary

    • Gross yielding: A fy/γM0 — ductile, visible, redistributes
    • Net fracture: 0.9 Anet fu/γM2 — brittle, sudden, local
    • The 0.9 is calibrated; the different partial factors reflect the consequence
    • In S355 about 14.9% of the area may be lost before fracture governs
    • It is the yield ratio fu/fy that decides, so a higher grade tolerates LESS
    • Compare gross yielding and net fracture for the actual material values, hole pattern and applicable factors
    • Block tearing adds a fracturing tension face to yielding shear faces
    • Block tearing is found by neither the member check nor the bolt check