The Chartership Forum

Structural Steel Design / Multi-storey steel buildings

Floor systems, and the multiplication

The decision that matters is the floor zone, not the beam depth — and whatever you decide, you will pay for it once per storey.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Corrections checked in this pass

  • Ratio examples distinguish braced-frame and core baselines; illustrative ratios no longer presented as transferable structural properties, and ductility is not assigned solely by system label.

Checks needed for project use

  • A steel-design reviewer must check the first-generation calculation profiles, second-order analysis assumptions, connection rules and execution references against the applicable standards and amendments.
  • Actual geometry, cracked stiffness, connection behaviour, lateral analysis and applicable global stability criterion.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

A multi-storey building is the same floor, repeated. That sounds obvious and it changes everything about where design effort belongs: a decision made once about how a floor is built is then paid for on every storey, in cladding, in services, in lift travel and in whether the building fits under a planning height. The single most consequential number in the whole design is one that is fixed before any member is sized — the floor zone — and getting it right requires comparing systems on a quantity most people do not compare them on.

By the end of this lesson you should be able to

  • Compare floor systems on zone rather than depth
  • Say why services through the structure change the answer
  • Multiply a per-floor saving through a building
  • Apply the imposed-load reduction correctly

What you should already know

  • Composite beams and their construction stages (Module 11)
  • Load combinations and the imposed-load family (Module 2)
  • Cellular and castellated sections as a member type (Module 5)

The floor zone, not the beam depth

The question a floor system has to answer is not "how deep is the beam?" but "how much of the building's height does this floor consume?" That is the floor zone:

floor zone = structural depth + services below the structure + finishes

And the middle term is where systems differ most, because some let the services pass through the structure and some do not.

For a 12 m span, with 400 mm of services and 250 mm of finishes:

SystemStructureServices belowFloor zoneSteel
Downstand composite500 mm400 mm1150 mm40 kg/m²
Slab on beams667 mm400 mm1317 mm55 kg/m²
Cellular beam600 mm0850 mm45 kg/m²
Integrated (slim floor)429 mm0679 mm55 kg/m²

Read the third and first rows against each other:

The cellular beam is 100 mm deeper than the downstand composite beam, and its floor zone is 300 mm shallower.

That is the whole argument. A designer comparing beam depths would choose the downstand and lose 300 mm per storey. The ducts have to go somewhere, and a system that gives them a hole to go through has already paid for its extra depth several times over.

Try it

Floor zone, and what it is worth multiplied

Four floor systems, drawn as structure (solid) plus the services that have to go beneath it (hatched). The bar length is the floor zone — the quantity that actually consumes building height.

12.0 m
400 mm
10

Compare against the downstand

Floor zone by system, split into structure and services belowdownstand composite1150integrated679cellular850slab on beams1317solid = structure · faded = services that must go beneath itsaving 300 mm per floor · 3.00 m over 10 storeys
Downstand structural depth
500 mm
Downstand floor zone
1150 mm
Alternative structural depth
600 mm
Alternative floor zone
850 mm
Deeper structure?
yes
Shallower floor?
yes
Saving per floor
300 mm
Height saved
3.00 m
Façade saved
420 m²
Cladding saved
£294k
Extra steel
60 t
Steel cost
£132k
Net
£162k

300 mm saved per floor becomes 3.00 m over 10 storeys — 420 m² of façade that need not be bought. Against that, 60 tonnes more steel. The net is in favour of the shallower option, and it is close enough that the real decision usually turns on something else — a planning height limit, a lettable-area calculation, or the programme.

Things worth trying

  • Start with the cellular option at 12 m span. Its structure is 100 mm DEEPER than the downstand and its floor zone is 300 mm shallower, because the ducts go through it.
  • That 300 mm is 3.0 m over ten storeys, 420 m² of façade and £294k — against 60 tonnes of extra steel at £132k. Net £162k in favour.
  • Now switch to the integrated floor. It saves MORE height — 4.71 m — and delivers LESS net value, because its steel penalty is three times larger.
  • That is the point: the quantity to optimise is the net, and it has two terms moving in opposite directions. The shallowest system is not automatically the right one.
  • Take the service depth down to 150 mm. The downstand catches up sharply, because the thing it was losing on has shrunk. On a lightly serviced building the simple solution wins.
  • Now take it to 700 mm — a heavily serviced laboratory or hospital. The gap widens dramatically and the through-structure systems become almost unarguable.
  • Increase the storeys to 30 and watch every figure scale. The decision does not change, but its importance does: the same 300 mm is now 9 m of building.
  • Try the slab-on-beams option. It is deeper AND has services beneath it, so it loses on both terms — which is why it is used for its other virtues, not for its depth.

Worked example

Choosing a floor system for a ten-storey office

Given

  • Ten storeys, 1200 m² per floor, 140 m perimeter
  • 12 m clear span between columns, 400 mm of services, 250 mm of finishes
  • Cladding £700/m², steel £2200/tonne erected
  • Compare downstand composite, cellular and integrated

Find

Which floor system to adopt, and on what grounds.

Assumptions

  • Span-to-depth ratios and steel rates are engineering recommendations, not code values
  • Cladding and steel rates are illustrative; a real comparison would be priced
  • The comparison ignores fire protection, which favours systems with less exposed steel

    Load take-down, and why the reduction exists

    A column low in a building carries the floors above it. The permanent load simply accumulates — ten floors of concrete weigh ten times one floor of concrete.

    The imposed load does not, and the reason is probabilistic. The chance that all ten floors are simultaneously at their full design imposed load is very small. The reduction factor acknowledges that:

    Storeys carriedαnImposed load
    11.00090 kN
    30.900243 kN
    50.820369 kN
    100.760684 kN

    For the worked column at 120 kN permanent and 90 kN imposed per storey, the lowest column takes 1884 kN against 2100 kN unreduced — 10% less.

    Notice why the total reduction is only 10% when the factor is 0.76: the reduction applies to the imposed part only, and on this column the permanent load is the larger of the two. A column under a lightly loaded roof and heavy floors would gain much more; a column carrying mostly self-weight would gain almost nothing.

    αn is a nationally determined parameter and is unverified in this course, so the calculation is teachable and not usable. What is worth carrying regardless is what it is FOR — it is a statement about probability, not about strength, and it is the one place in a load take-down where the answer is smaller than the sum of its parts.

    Practice

    A 12 m span cellular beam is 600 mm deep with services through it, plus 250 mm of finishes. What is its floor zone, in mm?

    Practice

    300 mm is saved per floor on a ten-storey building. How much building height is saved, in m?

    Practice

    That 3.0 m is saved on a building with a 140 m perimeter. How much façade is saved, in m²?

    Practice

    A column carries 10 storeys. With αn = (2 + (n − 2) × 0.7)/n, what is αn?

    Check yourself

    Why does the imposed-load reduction exist?

    Summary

    • Compare floor ZONE = structure + services below + finishes, not beam depth
    • A 600 mm cellular beam gave 850 mm of zone; a 500 mm downstand gave 1150
    • 300 mm per floor × 10 storeys = 3.0 m = 420 m² of façade = £294 000
    • It cost 60 t of extra steel, so the net was £162 000 in favour
    • The integrated floor saved MORE height and delivered LESS net value
    • So the quantity to optimise is the net, which has two opposing terms
    • Imposed-load reduction is a probability statement: αn = 0.76 over ten storeys
    • It applies to the imposed part only — the worked column's total fell just 10%