The Chartership Forum

Structural Steel Design / Structural steel as a material

Residual stress, thickness and toughness

Three properties that are invisible in a tensile test, absent from most calculations, and responsible for a surprising share of what goes wrong.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Checks needed for project use

  • A steel-design reviewer must check the first-generation calculation profiles, second-order analysis assumptions, connection rules and execution references against the applicable standards and amendments.
  • Residual-stress examples use idealised elastic-perfectly-plastic fibres. Actual buckling-curve selection and product-thickness strength values need standards verification.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

A steel member arrives on site already stressed, before any load is applied. Its strength depends on how thick it is, which the grade name does not tell you. And it can fail in a way the tensile test never shows — suddenly, at low stress, with no yielding at all. None of these appears in a routine calculation, and all three change design decisions.

By the end of this lesson you should be able to

  • Explain where residual stresses come from and why they matter for buckling
  • Say why thicker product has a lower nominal yield strength
  • Distinguish toughness from strength and from ductility
  • Recognise lamellar tearing as a through-thickness problem, not a weld problem

Steel is already stressed before you load it

A hot-rolled section leaves the mill at around 1000 °C and cools in air. It does not cool evenly. The flange tips and the outside surfaces are exposed on more sides, so they cool first; the web–flange junction is buried in the middle of a mass of hot steel and cools last.

The parts that cool first contract first, and set. The parts that cool later then try to contract, and cannot — the already-solid material is in the way. So the late-cooling regions end up in tension, and to balance them the early-cooling regions end up in compression.

For a rolled I section that means:

  • flange tips in residual compression, typically 30% of fy or so;
  • web–flange junction in residual tension;
  • the whole pattern self-balancing, because no external load is applied.

Welding does the same thing far more sharply. A weld is a small volume of molten metal cooling against a large cold mass, so it contracts hard and ends up in high residual tension — often right up to yield — with compression balancing it nearby.

Residual stresses do not reduce the squash load. Add up the pattern and it sums to zero. What they do is make part of the section yield early.

Worked example

Where the flange tips start yielding

Given

  • A rolled I section in S355
  • Residual compression at the flange tips of about 0.3 fy
  • Residual tension at the web–flange junction, balancing it

Find

The applied stress at which the flange tips first yield, and what it means.

Assumptions

  • An idealised residual pattern — real distributions are measured and vary
  • The 0.3 fy figure is typical of rolled sections and is not a code value

    Thicker steel is weaker

    The grade name gives one number. The material does not.

    S355 means 355 N/mm² of yield strength — for product up to a stated thickness. Above it, the guaranteed value falls, to about 335 N/mm² and then further for very thick material.

    The reason is the same cooling story. Thick product cools more slowly, which produces a coarser grain structure, and it receives less rolling reduction, which does less to refine that structure. Fine grains resist dislocation movement; coarse grains resist it less. So thicker material is genuinely weaker, not conservatively rated.

    Two consequences catch people out:

    A thick flange and a thin web may have different strengths in the same section. The classification of the flange and of the web then use different ε values, which is fiddly and is easy to miss.

    Thickness hurts twice. A thick-flanged section has lower fy and takes a worse buckling curve, because it also cooled more unevenly. The two effects compound.

    Try it

    What the grade name does not tell you

    Choose a grade and a thickness, and watch two things move in opposite directions: the strength you can use goes up, and the slenderness you are allowed goes down. Specifying a stronger steel is not a free improvement.

    Steel grade

    15 mm
    60
    Class bands for an internal element in bendingClass 15968Class 3101Class 4c/t = 60internal element in bending · limits are 72ε, 83ε, 124εε = 0.814 · every band moves when the grade changes
    Nominal strength for the grade
    355 N/mm²
    Strength at this thickness
    355 N/mm²
    Thickness reduction applied
    no
    ε = √(235/fy)
    0.814
    Class 1 limit
    58.6
    Class 2 limit
    67.5
    Class 3 limit
    100.9
    Element class
    Class 2

    Class 2: the plastic modulus Wpl may be used — though not plastic analysis, because the rotation capacity is limited.

    Things worth trying

    • Fix c/t at 75 and raise the grade from S235 to S460. The element goes from Class 2 to Class 3 or worse with NO change of geometry. Stronger steel makes local buckling more likely — this is the single most counter-intuitive result in cross-section design.
    • Raise the thickness past 40 mm and watch two things happen at once: the usable strength falls, and ε rises so the limits get slightly more generous. The weaker steel is easier to classify, which is a small consolation.
    • Set the grade to S235 and note that ε = 1.000 exactly. S235 is the reference grade the limits were written for, which is why 235 appears in the formula at all.
    • Push c/t past the Class 3 limit. Nothing physically dramatic happens at that line — it is a calibrated design boundary, not the slenderness at which the plate actually buckles. What changes is which resistance you are allowed to claim.

    Toughness: a different failure mode entirely

    Everything so far has been about yielding. Toughness is about not yielding — about a crack running through material that never gets the chance to deform.

    Brittle fracture needs three things at once:

    1. 1.A flaw — a notch, a crack, a sharp re-entrant corner, a weld defect.
    2. 2.Tensile stress across it.
    3. 3.Low toughness, which means low temperature, high thickness, or high strain rate.

    Given all three, a crack can run across a member at close to the speed of sound, at a stress well below yield, with no warning and no visible deformation. It is not a ductile failure that happened quickly; it is a different mechanism.

    Toughness is measured by a Charpy test — the energy absorbed breaking a notched specimen — and the striking feature is the transition. Above a certain temperature the specimen absorbs a lot of energy and tears; below it the specimen absorbs very little and snaps. The change happens over a few tens of degrees.

    So steel is specified not only by strength but by a sub-grade: the J and K designations record the temperature at which a stated Charpy energy is achieved. Choosing a sub-grade is choosing where that transition sits relative to the coldest temperature the structure will see.

    Practice

    A rolled section in S355 has residual compression at the flange tips of 0.25 fy. At what applied stress do the tips first yield, in N/mm²?

    Practice

    A 70 mm thick S355 plate is used as a flange. Taking the reduced nominal strength as 335 N/mm², what is ε for classifying that flange?

    Practice

    Comparing S235 and S460, by what factor do the classification limits (which are multiples of ε) tighten?

    Check yourself

    Residual stresses in a rolled section sum to zero over the cross-section. Why do they still matter?

    Summary

    • Residual stress comes from uneven cooling: early-cooling regions end in compression, late in tension
    • The pattern sums to zero, so the SQUASH load is unaffected
    • But the flange tips yield early, and they are the fibres that matter most about the minor axis
    • That is the physical content of the buckling curve selection table
    • Welding produces a far sharper pattern than rolling, hence a worse curve
    • Thicker product has a lower nominal yield strength — the grade name is not enough
    • Toughness is a separate failure mode: flaw plus tension plus low temperature
    • Lamellar tearing is a DETAILING fault, not a weld fault — the load runs through the plate thickness