The Chartership Forum

Structural dynamics / tutorial

A pressure pulse on a wall panel

The duration relative to the period decides everything about a short load.

Return to tutorials
Teaching basis and review status

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

A wall panel is to be checked against a short pressure pulse from an accidental release in an adjacent plant room. The pulse can be idealised as rectangular. The panel's period is fixed by its span and construction; the pulse duration is not well known, so the answer must be given as a function of it.

  • Panel treated as a single-degree-of-freedom system, undamped for this check
  • Rectangular pressure pulse of duration td
  • Three candidate durations: td/Tₙ = 0.2, 0.5 and 2.0

Practice

First, the reference case: what is the dynamic load factor for a load applied suddenly and held indefinitely, on an undamped system?

Practice

What is the peak dynamic load factor for a rectangular pulse with td/Tₙ = 0.2?

Practice

And what is the peak dynamic load factor for a pulse of duration td/Tₙ = 0.5?

Practice

And for a much longer pulse, td/Tₙ = 2.0 — what is the peak dynamic load factor?

The whole answer is decided by one ratio, and the panel's period is the engineer's lever on it. A stiffer panel has a shorter period, which RAISES td/Tₙ and moves it towards the plateau — so stiffening a panel against a short pulse can increase the demand on it. That is the opposite of the static intuition.